Vibration warning msg

1

Enter image description here
Enter image description here

We need to understand why the system only sent us a warning msg at 15:40 once three readings higher than the warning threshold were detected before (11:40, 13:40, 14:40)? Could you please explain why we only receive the warning msg at 15:40 and not at 11:40? See the pictures attached showing the readings.

Marcos
posta 4 mesi fa177 visualizzazioni
1 Risposta
0
Risposta accettata

Hi Marcos,

Monitron looks at number of measurements within a time window before switching the state from HEALTHY to WARNING or ALARM. This is what you have observed in your screenshot, and is to ensure an alert isn't triggered from an anomalous measurement.

Hope this provided some clarity.

AWS
Gary_S
con risposta 4 mesi fa